       铅酸蓄电池充电间内的防爆设备包含线缆配管吗?图纸设计电池室的明敷线缆的保护管为JDG管敷设,是否复合规定?同时,其明敷线缆保护管设计为SC型配管,有强条规定吗?电池室排风设计为独立排风,且设计了换气设备,排氢气很通常。感谢老师解答

1200xt | 2025-05-26 09:58
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

牛丫头消防课堂 2025-05-26 17:46 10 [回复]举报

建议你翻翻《建筑电气与智能化通用规范》 GB55024-2022第3.2.5条, 专用蓄电池室应采用防爆型灯具,室内不得装设普通型开关和电源插座。

条文说明:3.2.5 专用蓄电池室因爆炸危险性较高,所以规定有电气连接的照明、开关、电源插座等,安装在室内时应采用防爆型产品,否则应安装在室外。

按照这条理解室内的应该是防爆的,而且是强制性条文。

1200xt   回复: 牛丫头消防课堂2025-05-27 12:02

谢谢老师解答,很清晰。受教了