消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水泵启动问题

一个做现场的工程师跟我讲:水泵联动启动是主机通过总线控制盘启动的,多线控制盘只是手动启动消防水泵,如果水泵不连接总线盘,那么水泵就没有办法联动启动,请问这种说法正确不?

姜子牙疼 | 2022-04-11 11:15
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 6

消防网友78337 2022-04-11 13:52 00 [回复]举报

如果水泵不连接总线盘,那么水泵就没有办法联动启动,这是不对的。


简单说,存在有消防泵房,无消防控制室(无火灾自动报警系统)的建筑,如何启动消防泵。


按火灾自动报警系统设计规范要求,消防泵是可以通过水流指示器或压力开关启动的


4.3.1 联动控制方式,应由消火栓系统出水干管上设置的低压压力开关、高位消防水箱出水管上设置的流量开关或报警阀压力开关等信号作为触发信号,直接控制启动消火栓泵,联动控制不应受消防联动控制器处于自动或手动状态影响。当设置消火栓按钮时,消火栓按钮的动作信号应作为报警信号及启动消火栓泵的联动触发信号,由消防联动控制器联动控制消火栓泵的启动。


具体还可见相关图集。


姜子牙疼   回复: 消防网友783372022-04-11 16:04

有联动型的火灾自动报警系统,我以前的理解是重要的设备接多线,次要的接总线,联动的时候,报警控制器将满足逻辑关系的信号发给多线去启泵,发给总线去控制防火门,卷帘等设备

按照现场的这种做法,是符合逻辑后,报警控制器将信号传递给总线盘,然后总线盘执行启泵命令,而不是发给多线盘去执行启泵命令,是这样吗?

这样的话,总线盘上面也有一个跟卷帘一样的用于水泵的节点吗?

联动启动后多线盘的水泵启动和反馈指示灯会亮不

0    0 [回复]举报

牟青 2022-04-11 16:09 00 [回复]举报

可以直接通过水泵控制柜连锁启泵

布鲁斯 2022-04-11 21:50 00 [回复]举报

























































姜子牙疼   回复: 布鲁斯2022-04-12 08:51

我说的是接线问题,水泵跟总线控制盘有没有接线

0    0 [回复]举报

乌伤浪人 2022-04-17 23:48 00 [回复]举报

首先回答你提问的说法是错误的。火规有关消防联动控制的一般规定明确规定,任何需要联动控制的设备都必须具备总线联动控制模式;其它的联动控制设计要求规定了重要的消防设备还应该设置专线控制(远程、多线控制)。消防泵的联动控制可以通过报警控制器编程由总线模块联动控制或专线控制。

关闭

关闭

手机APP下载