商场店铺上下开楼板,加楼梯,新增防火卷帘的长度要求?

多层商场内,上下2层店铺开楼板,加楼梯连通,楼梯不做疏散通道,二层楼梯口一周防火卷帘的长度要求?

杜浒 | 2022-04-18 11:22
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

消防网友78337 2022-04-18 14:14 10 [回复]举报

GB50016-2014其中6.5.3 -1除中庭外,当防火分隔部位的宽度不大于30m时,防火卷帘的宽度不应大于10m;当防火分隔部位的宽度大于30m时,防火卷帘的宽度不应大于该部位宽度的1/3,且不应大于20m。

你的情况可认为是中庭,新增防火卷帘无长度限制要求,就是一圈全部设置成防火卷帘。

这种打穿楼板的装修,需要原设计单位核定,进行变更设计。