泰和安主机报输出线故障

3016A泰和安主机,多线盘送风机、排烟机报输出线故障,但多线盘可以正常启停送风机、排烟机,请问可能是什么原因导致的故障?


| 2022-08-24 12:01
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

李勤 2022-08-26 13:13 20 [回复]举报

微阻松动或损坏(微阻应该按在模块内,检查线路通断功能)

  回复: 李勤2022-09-01 19:53

谢谢

0    0 [回复]举报

  回复: 李勤2022-09-01 19:53

谢谢

0    0 [回复]举报

阳明心 2023-05-16 13:40 00 [回复]举报

标准检线电阻应该接线设备末端,而非模块内。根据我的观察现场有很多施工的将检线电阻接在模块内,那样其实就失去了检线的作用,因为回路在模块端就形成,与设备间的线就无关了。   


                                                                                                            