消防水泵流量选取

各位老师们好!想请教一个问题:

最近在做毕设,是一个建筑群,假设A子项建筑的消防用水量最大,q喷淋=30l/s,B子项的消防用水量不如A子项的大,但是q喷淋=50l/s。请教各位老师,喷淋泵选取流量的时候,是用A子项的还是B子项的?用B子项的话,那水量不就不够了吗?

小月半 | 2023-01-12 10:12
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 11

张牙舞爪的张 2023-01-12 13:30 00 [回复]举报

选B。建筑群内消防水池是环状共用的,消防用水量只需要满足建筑群内最大建筑消防用水量;喷淋管道一致情况下也需要满足最大建筑喷淋用水量。

小月半   回复: 张牙舞爪的张2023-01-12 16:10

老师,那这样的话,在活在延续时间内,消防水池的用水量还够吗?

0    0 [回复]举报

刘凡   回复: 小月半2023-01-12 17:31

就是要根据喷淋系统的消防用水量、消火栓系统的消防用水量去确定消防水池的容积  

0    0 [回复]举报

张牙舞爪的张   回复: 小月半2023-01-12 21:54

建筑群默认只会发生一起火灾,因此,满足最大建筑用水量即可。

0    0 [回复]举报

小月半   回复: 张牙舞爪的张2023-01-13 10:37

那B子项发生火灾的时候,喷淋泵的流量不就不够了吗?

0    0 [回复]举报

小月半   回复: 刘凡2023-01-13 10:38

那B子项发生火灾的时候,喷淋泵的流量不就不够了吗?

0    0 [回复]举报

张牙舞爪的张   回复: 小月半2023-01-13 12:30

建筑群内采用50L/S流量的喷淋泵,建筑群组共用消防设施下,无论A或B建筑着火情况下,都满足;消防用水量在火灾情况下,满足建筑最大消防用水量,这样无论A或B建筑着火,都满足的呀。火灾发生,喷淋泵运转,为其中一栋建筑灭火提供压力、流量,为什么不够呢?是够的。

0    0 [回复]举报

小月半   回复: 张牙舞爪的张2023-02-27 18:03

老师,我看有人说A的,有点混乱。。

0    0 [回复]举报

南明离火 2023-01-12 17:09 00 [回复]举报

选A,算总用水量,A建筑、B建筑总用水量单独计算,室内消火栓+喷淋+室外栓用水量+……哪个值大取哪个

小月半   回复: 南明离火2023-01-13 10:37

那B子项发生火灾的时候,喷淋泵的流量不就不够了吗?

0    0 [回复]举报

南明离火   回复: 小月半2023-01-13 12:52

够的,消火栓用不了那么多,分一部分给喷淋

0    0 [回复]举报