消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

住宅敞开楼梯间内能不能设水电管井

《建筑防火通用规范》GB 55037-2022第7.1.8条第5小条:除疏散楼梯间及其前室的出入口、外窗和送风口,住宅建筑疏散楼梯间前室或合用前室内的管道井检查门外,疏散楼梯间及其前室或合用前室内的墙上不应设置其他门、窗等开口。规范条文说明处7.1.8条中:在住宅建筑的楼梯间中允许设置水表、电表、气表、可燃气体管道等; 请问根据上述规范规范要求住宅开敞楼梯间内能不能设置水、电管井门;

馒头 | 2023-06-20 10:34
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 7

同同不同 2023-06-14 06:39 10 [回复]举报

安洪全 2023-06-14 08:37 00 [回复]举报

“住宅开敞楼梯间内能不能设置水、电管井?”

楼梯间内没法设置管井,但是可以将管井贴邻楼梯间设置。


或者您问的是能不能将管井门设于楼梯间内?

“《建筑防火通用规范》GB 55037-2022第7.1.8条第5小条:疏散楼梯间及其前室的出入口、外窗和送风口,住宅建筑疏散楼梯间前室或合用前室内的管道井检查门外,。。。。。。


hnlyplszq 2023-06-14 11:05 00 [回复]举报

住宅敞开楼梯间内能设水电管井,还有很多住宅是这样的。

消防网友78337 2023-06-14 11:49 10 [回复]举报

《建筑防火通用规范》GB 55037-2022第7.1.8条第5小条及其条文解释

《建筑设计防火规范》 GB50016-2014(2018年版)第6.4.1条

结合一述两条,可以认为在住宅开敞楼梯间内能不能设置水、电管井间(采用丙级防火门);

综合分析《建筑防火通用规范》GB 55037-2022第7.1.8条条文解释,其中说明了可以的内容和禁止的内容:

——除住宅建筑受平面布置限制需要将电缆井和管道井的检查门设置在前室或合用前室内外,在其他建筑的防烟楼梯间前室或合用前室内,不允许开设除疏散门和排烟窗以外的其他开口和管道井的检查门。


只有住宅能将管道井的检查门设置在前室里,不能设置在楼梯间内。

其它公共建筑管道井的检查门不能设置在前室,只能设置在前室外的走廊上的房间里,管道井的检查门开向走廊。

南明离火 2023-06-15 16:39 00 [回复]举报

可以  要不然 没地方放啊

风无心 2023-06-15 21:56 00 [回复]举报

《火通规》已经很明确了,楼梯间内都不能设其他开口了。

BCWP 2024-07-25 10:09 00 [回复]举报

可以。


7.1.8  5 除疏散楼梯间及其前室的出入口、外窗和送风口,住宅建筑疏散楼梯间前室或合用前室内的管道井检查门外,疏散楼梯间及其前室或合用前室内的墙上不应设置其他门、窗等开口---是用来限制封闭楼梯及防烟楼梯间。 -


---如果敞开楼梯间也按照此条执行,那么你连入户门都不能开在敞开楼梯间里了。

水电井必须设置在公共区域,多层住宅的公共区域通常只有楼梯间,如果必须封闭,那么敞开楼梯间也就失去了意义。

关闭

关闭

手机APP下载