一个报警阀可以带两种流量系数的喷头吗?

好难呀 | 2023-11-16 08:43
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

安洪全 2023-11-16 09:53 10 [回复]举报

可以啊,但同一隔间内应是同一种型号、规格、安装方式的喷头。

南明离火   回复: 安洪全2023-11-18 11:49

如果是厨房内呢,见过厨房内一个区域是93度,其他区域设置68°

0    0 [回复]举报

安洪全   回复: 南明离火2023-11-20 09:37

自动喷水灭火系统设计规范 GB50084-2017

6.1.8 同一隔间内应采用相同热敏性能的洒水喷头。


条文说明:

6.1.8 同一隔间内采用热敏性能、规格及安装方式一致的喷头,是为了防止混装不同喷头对系统的启动与操作造成不良影响。曾经发现某一面积达几千平方米的大型餐厅内混装Ф8和Ф5玻璃球喷头及某些高层建筑同一场所内混装下垂型、普通型喷头等错误做法。


个人理解:

混装可能导致温度低的喷头先动作,喷放的水量虽不足以灭火,但又使温度持续达不到高温度喷头的动作要求,致使火情的蔓延,故又此规定。

0    0 [回复]举报

我的是昵称 2023-11-17 16:13 00 [回复]举报

这个没要求,可以的。只有在一个灭火单元内或一个房间内是不能有两种。