消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

楼板多处开洞,防烟分区可以跨越楼层吗?

丙类工业厂房,两层之间的楼板有多处开洞,两层可以划分为一个防烟分区吗?

旺旺 | 2023-11-17 13:51
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 8

阳明心 2023-11-17 14:12 00 [回复]举报

防烟分区不能跨越防火分区,两层如果不是同一个防火分区的,不可以

如果两层本来就是同一防火分区的,那防烟分区的面积不超规定,可以

旺旺   回复: 阳明心2023-11-17 14:35

两层为一个防火分区。两层的层高为10米,两层算一个防烟分区的话,净高可以按照10米算吗?

0    0 [回复]举报

阳明心   回复: 王meimei2023-11-17 14:57

可以的

0    0 [回复]举报

南明离火   回复: 旺旺2023-11-18 14:58

不可以,你下面的烟气透过这些开孔往上层飘要把上层的熏死啊

0    0 [回复]举报

我的是昵称 2023-11-17 16:23 00 [回复]举报

除了中庭外,防烟分区不能跨越楼层,更不能跨越防火分区。烟气是高温的,你跨越防火分区,岂不是把相领的防火分区给引燃了?而且防烟分区还有长度和面积要求,如果是自然排烟,还要排烟口的面积,你怎么算?

yizhongdayang 2023-11-18 10:55 00 [回复]举报

《建筑防烟排烟系统技术标准》 GB51251-2017/4.2.3条文说明:上、下层之间应是两个不同防烟分区,烟气应该在着火层及时排出,否则容易引导烟气向上层蔓延的混乱情况,给人员疏散和扑救都带来不利。在敞开楼梯和自动扶梯穿越楼板的开口部位应设置挡烟垂壁或卷帘,以阻挡烟气向上层蔓延,不得叠加计算防烟分区。

2023-11-18 11:10 00 [回复]举报


关闭

关闭

手机APP下载