消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟阀连锁

排烟执行器或排烟口(排烟阀)关闭后排烟风机是否也停止?

吴猛 | 2023-12-26 08:41
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

安洪全 2023-12-26 13:07 00 [回复]举报

建筑防烟排烟系统技术标准 GB51251-2017

4.4.6 排烟风机应满足280℃时连续工作30min的要求,排烟风机应与风机入口处的排烟防火阀连锁,当该阀关闭时,排烟风机应能停止运转。

条文说明:

4.4.6 作为排烟风机应有一定的耐温要求,国内生产的普通中、低压离心风机或排烟专用轴流风机都能满足本条要求。当排烟风道内烟气温度达到280℃时,烟气中已带火,此时应停止排烟,否则烟火扩散到其他部位会造成新的危害。而仅关闭排烟风机,不能阻止烟火通过管道的蔓延,因此本条规定了排烟风机入口处应设置能自动关闭的排烟防火阀并连锁关闭排烟风机。

阳明心   回复: 安洪全2023-12-26 15:14

通辽老师,他问的是排烟阀(排烟口),不是排烟防火阀,请您重新回答一下,谢谢

0    0 [回复]举报

消防网友42325   回复: 阳明心2023-12-27 08:35

排烟阀·就是排烟防火阀

0    1 [回复]举报

安洪全   回复: 阳明心2023-12-27 09:36

老师不敢担,一起探讨,共同进步。

我之所以回答排烟防火阀,就是能联动关闭排烟风机的,只有排烟风机入口处的防火阀具备这个功能,其他的设施不应该联动关闭对应的排烟机。

我认为理由有两个,一个是联动关闭可能在火灾情况下出现误都做动作,不利火灾时的排烟;二是一个排烟风机可能带多个排烟口,一个排烟口的烟气温度达到关闭,不代表其他位置不需要排烟,恰恰在一个防烟分区内,某个位置温度高,这个防烟分区内其他排烟口更应保持排烟,便于人员疏散。

0    0 [回复]举报

阳明心   回复: 安洪全2023-12-27 14:24

根据您的描述,我理解就是排烟执行器或排烟口(排烟阀)关闭后排烟风机不会停止。

0    0 [回复]举报

徐海金 2023-12-26 17:57 10 [回复]举报

不需要停止,因为不会存在这种情况!以前一段时间有做硬线连锁启动风机的时候,关阀会停止,只是试一下是不是硬线连的,联动的不会存在你这种情况,那如果平常测试的时候为什么不先停风机再关阀呢,没有必要去纠结这个!

潘天坤 2024-06-17 20:24 00 [回复]举报

烟规GB51251里面没有关闭排烟口停止排烟风机的要求

烟规GB51251要求连锁的部位在风机入口处的排烟防火阀

消防设施通用规范要求联锁的部位比较多,也有些争议,这边不做讨论

关闭

关闭

手机APP下载