层高大于24米的二类高层,6层以下的楼梯间是否可以设置为开敞楼梯间?

层高大于24米的二类高层,6层以下的楼梯间是否可以设置为开敞楼梯间?

老王老师 | 2024-03-12 11:27
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

后格风法 2024-03-12 16:48 00 [回复]举报

不可以,除非裙房与高层建筑主体之间设置防火墙时,裙房的疏散楼梯可按单、多层建筑的要求确定。

马先生 2024-03-12 18:22 10 [回复]举报

首先要确定是工业厂房、还是民用建筑;1;厂房:高层厂房和甲乙丙类多层厂房的疏散楼梯应采用封闭楼梯间或室外楼梯。2;住宅:建筑高度大于21m、不大于33m的住宅建筑应采用封闭楼梯间;当户门采用乙级防火门时,可采用敞开楼梯间。3;公共建筑:一类高层公共建筑和建筑高度大于32m的二类高层公共建筑,其疏散楼梯应采用防烟楼梯间。裙房和建筑高度不大于32m的二楼高层公共建筑,其疏散楼梯应采用封闭楼梯间。根据你的描述,只要需要设置封闭楼梯间的建筑,就要整栋楼梯间必须要设置为封闭楼梯间。不能分上下。

消防网友21314   回复: 马先生2024-03-18 08:33

都二类高层了,还要区分是不是民用建筑?


0    0 [回复]举报

奋斗的样子 2024-03-13 00:00 00 [回复]举报

安洪全 2024-03-13 08:31 10 [回复]举报

封闭楼梯间

建筑防火通用规范 GB55037-2022

7.4.5 下列公共建筑中与敞开式外廊不直接连通的室内疏散楼梯均应为封闭楼梯间:    

1 建筑高度不大于32m的二类高层公共建筑;    

2 多层医疗建筑、旅馆建筑、老年人照料设施及类似使用功能的建筑;    

3 设置歌舞娱乐放映游艺场所的多层建筑;    

4 多层商店建筑、图书馆、展览建筑、会议中心及类似使用功能的建筑;    

5 6层及6层以上的其他多层公共建筑。

Aris_Ji 2024-03-13 22:43 00 [回复]举报

1.工业建筑不可以,高层最少封闭楼梯间

2.不大于32米的二类高层公共建筑,当楼梯间与敞开式外廊相连可以采用敞开楼梯间

3.群房与主体之间没有防火墙,必须封闭楼梯间

4.裙房与主体之间有防火墙,不大于6层,且不是特定功能建筑(详见楼上表格)可以采用敞开楼梯间。如果与敞开式外廊相连可以采用敞开式。否则只能采用封闭式。