无吊顶楼板下可不可以安装下垂型喷头

因室内净高不足2.5m,无吊顶,可不可以安装下垂型喷头,做到溅水盘与楼层间距满足75-150mm呢?

消防网友58633 | 2024-05-13 13:20
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

消防检查 2024-05-14 09:00 00 [回复]举报

规范要求直立型。

一路同行 2024-05-14 10:12 10 [回复]举报

GB50084—2017第6.1.3.1条规定配水支管布置在梁下时应采用直立式喷头(重点是梁下)

安洪全 2024-05-14 13:15 00 [回复]举报

不可以

自动喷水灭火系统设计规范 GB50084-2017

6.1.3 湿式系统的洒水喷头选型应符合下列规定:      

1 不做吊顶的场所,当配水支管布置在梁下时,应采用直立型洒水喷头;      

2 吊顶下布置的洒水喷头,应采用下垂型洒水喷头或吊顶型洒水喷头;      

3 顶板为水平面的轻危险级、中危险级Ⅰ级住宅建筑、宿舍、旅馆建筑客房、医疗建筑病房和办公室,可采用边墙型洒水喷头;      

4 易受碰撞的部位,应采用带保护罩的洒水喷头或吊顶型洒水喷头;      

5 顶板为水平面,且无梁、通风管道等障碍物影响喷头洒水的场所,可采用扩大覆盖面积洒水喷头;      

6 住宅建筑和宿舍、公寓等非住宅类居住建筑宜采用家用喷头;      

7 不宜选用隐蔽式洒水喷头;确需采用时,应仅适用于轻危险级和中危险级Ⅰ级场所。

gx祥子 2024-05-14 17:04 00 [回复]举报

应该直立,否则管道不好安装了。

呼哈噜啦 2024-05-14 17:57 00 [回复]举报

不可以


周家斌 2024-05-15 08:55 30 [回复]举报

规范只对不做吊顶的场所,当配水支管布置在梁下时,应采用直立型洒水喷头的要求;做到溅水盘与楼层间距满足75-150mm的楼板下,可以设置下垂型。