消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

执行机构是否要硬拉线至排烟风机柜

现场好多都没拉线到排烟风机柜,那是通过什么方式启风机的呢,

消防网友40442 | 2025-06-24 09:10
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

罗马苏丹 2025-06-24 09:33 00 [回复]举报

加压送风机、排烟风机、补风机应具有现场手动启动、与火灾自动报警系统联动启动和在消防控制室手动启动的功能。

牛丫头消防课堂 2025-06-24 09:40 20 [回复]举报

您说的是排烟阀的执行机构吧,联动启动排烟风机就可以,不需要执行机构硬拉线至排烟风机柜。

规范依据: 《火灾自动报警系统施工及验收标准》 GB50166-2019第4.18.8条,

5 消防联动控制器接收到排烟口、排烟阀的动作反馈信号后,应发出控制排烟风机启动的启动信号;
6 风机控制箱、柜应控制排烟风机启动;

7 消防联动控制器应接收并显示排烟分机启动的动作反馈信号,显示设备的名称和地址注释信息,且控制器显示的地址注释信息应符合本标准第4.2.2条的规定;
8 消防控制器图形显示装置应显示火灾报警控制器的火灾报警信号、消防联动控制器的启动信号、受控设备的动作反馈信号,且显示的信息应与控制器的显示一致。

Along Niusk 2025-06-24 10:36 00 [回复]举报

1.需要搞清楚,什么设备的“执行机构”要拉线至排烟风机控制柜?——把问题描述清楚

2.风机控制控制柜是控制排烟风机的,需要受控的工况有:风机防火阀熔断后联锁关停/紧急情况现场手动启动按钮(控制柜+现场边墙)/消防联动控制器多线启动;

3.第2条的3种启动皆需独立敷线实现,建议现场逐一测试(如果在没有敷设现场手动启动线的前提下还能远程启动风机,可能是消防联动控制器上的多线启动按钮敷线接入了风险控制柜的接触器)

小唐12321 2025-06-24 11:20 00 [回复]举报

不需要,联动就好,执行机构模块信号,然后主机去启动排烟风机,不用连锁,连锁是启水泵,比如压力开关火低压压力开关用线直接拉到水泵控制柜,

李勤 2025-06-25 11:02 00 [回复]举报

潘天坤 2025-06-26 09:04 00 [回复]举报

常闭排烟口的手动操作装置,从规范来说是联动逻辑,这个位置不需要拉硬线,当然如果设计是设计控制线的话就按图执行


方式的话属于“现场手动开启功能”,要求是“系统中任一排烟阀或排烟口开启时,排烟风机、补风机自动启动”


机械排烟系统中的常闭排烟阀或排烟口应具有火灾自动报警系统自动开启、消防控制室手动开启和现场手动开启功能,其开启信号应与排烟风机联动


 系统中任一排烟阀或排烟口开启时,排烟风机、补风机自动启动




关闭

关闭

手机APP下载