今天本被一图审提了这样的问题,请问怎么破:

问题如下:

该设计防烟分区划分,其排烟量的变化(比较是否大于原设计的排烟量)及消防控制室、现场对排烟口、防火阀改动变化接入原设计系统,均应由原设计单位审核认可。


然后他的依据是下面这条……

建筑内部装修设计防火规范 GB50222-2017 >

4.0.1 建筑内部装修不应擅自减少、改动、拆除、遮挡消防设施、疏散指示标志、安全出口、疏散出口、疏散走道和防火分区、防烟分区等。

-------------------------------------------------------------------------------

我方愚笨,一直以来都是改变了防烟分区,做好相应的防火分隔措施及防烟措施,计算好排烟量、补风量,重新设计排烟管道、风口、甚至风机都可以,但是他这次提这种问题,如何是好呢?




查规范 | 2022-01-13 13:34
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

小马 2022-01-13 14:33 00 [回复]举报

这个只能去和审图的沟通,这一条根据实际情况来讲的话,是不太可能严格执行的,内部装修都是各装各的,很多施工队都是游击队,也不可能说不对原有的消防设施进行改动。。。而且你们重新设计也是有设计资质的,只要符合现行规范,那就不属于擅自减少改动吧。。。

查规范   回复: 小马2022-01-15 11:10

审图的是一位60多的返聘专家,阅历丰富,和他请教了半天,得出的答复还是需要原设计单位符合,并且盖章认可后才可以按我方设计执行。

0    0 [回复]举报

陈曲   回复: 查规范2022-01-18 17:50

相比之下这样是最简单 最省钱的 

0    0 [回复]举报

消防网友34346 2022-01-18 15:58 00 [回复]举报

改变分区涉及到火灾自动报警系统联动关系的改变,应该经过人家确认

GANSTER 2022-02-10 11:11 00 [回复]举报

这位审图大爷并未理解该条文的精神,还加上自我解读,任何规范都不会提到原设计单位什么事,只要你的变更符合程序,各专业都走正规设计并报施工图审查,就不存在擅自一说。假如原设计单位解散了,那这件事就还办不下去咋地?