消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

火灾报警控制器的回路点数量

火灾报警控制器(联动型)的设备上,是不是所有的回路都不能超过100点,还是有输出功能的模块回路不超过100点

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

李勤 2022-02-03 20:58 10 [回复]举报

报警回路200   ; 控制回路100  ; 报警和控制和混合回路  总点位不超过200(其中控制不超过100)------但是在施工中都在以上基础上减少10%作为机动预备量 ,其实就是90或180

剑胆琴心 2022-02-08 16:04 10 [回复]举报

火灾报警控制器回路和联动控制器回路不是一个概念,联动控制器回路是100,火灾报警控制器回路是200.分别留存10%的余量。供参考

关闭

关闭

手机APP下载