工业建筑3M净高的走道排烟量如何取值?

本次工程高层丙类厂房走道长度58.5m
根据《建规》第8.5.2-4条规定,应当设置排烟设施。且因装修布局原因,应当采用机械排烟。

但根据《排烟规》表4.6.3-3条规定,仅限制了公共建筑,未标明工业建筑。


想问工业建筑里3M净高的走道,机械排烟量最低为多少风量?

澜沐 | 2023-08-22 15:02
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

@mad 2023-08-23 15:29 00 [回复]举报

参考公共建筑的走道。

潘天坤 2024-06-20 21:42 00 [回复]举报

从规范角度可能存在问题

走道一般不考虑净高,然后排烟量一般为60*走道建筑面积且不小于13000

行业内一般觉得走道不考虑净高,同时规范没有提到工业建筑走道排烟的情况

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑